| CHANGE |
CODE
SECTION |
SUMMARY |
RECOMMEND |
COMMENTS |
| E1 |
1001.1 |
Makes
the statement that components of chapter 10 which are not
required for egress are not required to comply with the
chapter |
D |
Some
provisions of chapter 10 are necessary for safe use of
components whether required for egress or not |
| E2 |
1001.4 |
Requires
emergency planning and preparedness per the Fire Code |
D |
Not
appropriate for a construction code |
| E3 |
1002.1 |
Adds
unnecessary language to "accessible means of Egress" |
D |
|
| E4 |
1002.1 |
Adds
text to bleachers, grandstands, etc. consistent with ICC 300 |
AS |
Appropriate
change |
| E5 |
1002.1 |
Defines
"level of exit discharge" as a story not a plane |
AS |
In
the 33 instances of use in the code it is interpreted as story |
| E6 |
1002 |
Defines
"Flight" as "a run of stairs between
landings" |
AS |
The
term is used in the code |
| E7 |
1002.1 |
Defines
the term "walking surface" |
D |
Unnecessary
change |
| E8 |
1003.2 |
Adds
ramps to the exceptions for 7'-6" ceiling height |
AS |
Seems
appropriate, similar to stairs |
| E9 |
1003.2 |
Deletes
Section1003.2 |
? |
Proponent
is correct it is redundant, but not sure it hurts anything to
leave as is. |
| E10 |
1003.3 |
Requires
aisles in electrical and mechanical rooms to be striped where
the 80" minimum headroom is maintained |
D |
Does
not appear necessary. Do
all parts of the floor with over 80" get striped? |
| E11 |
1003.3.2-1003.3.4 |
Allows
projections into egress width at stairs and ramps only on the
run of the stair or ramp (not at extensions) |
? |
|
| E12 |
1003.8 |
Moves
requirements for access to rooftop equipment to the egress
section |
D |
Proponent
makes a good point that building construction related items
should be in the IBC and not in the IMC, but I'm not sure it
is an egress issue. |
| E13 |
1004.1 |
Changes
the application of the section for determining occupant loads
for all purpose, not only egress |
D |
Not
necessary |
| E14 |
1004.3 |
Requires
occupant load posting for E uses |
AS |
OK |
| E15 |
1005.1 |
Changes
"capacity" to "width" |
D |
Egress
width and capacity are not interchangeable.
50% of the width of a stair is not the same as 50% of
the width of a door with regard to capacity. |
| E16 |
1005.1 |
Revises
table to say "not permitted" for H1-H4 occ. and I-2
occ. |
AM |
The
values in the table are intended to be egress width per
occupant. "Not
permitted is not aproper answer to egress width in the table.
"NA" is more appropriate. |
| E17 |
1005.2 |
Discounts
the encroachment of hardware on required egress width. |
D |
Contrary
to the proponents statement, hardware has been considered when
considering door encroachments |
| E18 |
1005.2,
1014.4, 1017.2, 1021.2, 1024.5 |
Clarifies
door encroachment allowances in 1005.2 and then refers to this
section from other sections with the same language. |
AM |
Most
of the change seems appropriate, except not sure why handrails
are included with regard to door encroachment. |
| E19 |
1007.1 |
Alludes
to other sections of the code for accessible means of egress |
D |
Awkward
language, sounds as if all sections of Chapter 10 apply to
handicap. |
| E20 |
1007.1 |
When
two accessible means of egress are required, requires that
they be remote per 1015.2 |
AS |
Appropriate
change |
| E21 |
1007.1 |
Changes
exception to 2 accessible means of egress for assembly seating
with sloped floors. |
D |
Not
sure where stepped aisles fits into accessible means of
egress. |
| E22 |
1007.2 |
Inserts
1018 for 1020 and 1023 in requirements for continuity and
components of accessible means of egress |
AS |
Seems
appropriate |
| E23 |
1007.2,
1007.3, 1007.6, 1007.6.2 |
Reorganizes
some exceptions for accessible means of egress |
AS |
Seems
an appropriate change |
| E24 |
1007.3 |
Removes
the requirement for area of refuge in any stair within a
sprinklered building |
? |
Has
changed back and forth a few times |
| E25 |
1007.3,
1007.4 |
Removes
the requirement for area of refuge in any stair or elevator
within a sprinklered building |
? |
See
E24 |
| E26 |
1007.3 |
Area
of refuge or horizontal exits not required where all portions
of the means of egress are "essentially open to the
outside" |
D |
Not
sure why horiz. exits were included and "essentially open
to the outside" is vague language |
| E27 |
1007.4 |
Adds
exception to area of refuge to accessible egress elevators for
those not enclosed in a shaft and those where
"essentially open to the outside" |
D |
Same
vague language |
| E28 |
1007.3,
1007.4, 1007.7 |
First
part eliminates area of refuge for smoke protected seating |
D |
Should
probably read "when serving smoke protected
seating". The
last part of the change could be a logistical problem |
| E29 |
1007.3 |
Exempts
R-2 from requirement for area of refuge |
D |
Proponent
makes the argument that the sprinklered apartments serve as
areas of refuge. Unrealistic
expectation for emergency service personnel to attempt to
determine which apts need handicap assistance |
| E30 |
1007.3 |
Allows
exception for area of refuge for unenclosed stairs in
buildings protected by NFPA 13R systems |
AS |
Provisions
of NFPA 13R for
common areas are as required for NFPA 13. |
| E31 |
1007.6 |
Deletes
maximum travel distance required to an area of refuge |
? |
Proponent
makes a good argument about the travel distance requirement
greatly increasing the number of accessible means of egress
required in larger buildings, but should travel distance be
unlimited to an accessible means of egress? |
| E32 |
1007.6,
1007.6.2, |
Refers
to 707.14.1 for elev. Lobby |
AS |
Seems
like appropriate change |
| E33 |
1007.6 |
Similar
to E32 |
? |
Listen
to testimony to determine in E32, E33 or E34 are appropriate |
| E34 |
1007.6 |
Similar
to E32 |
? |
Listen
to testimony to determine in E32, E33 or E34 are appropriate |
| E35 |
1007.6 |
Similar
to area of refuge exceptions for 1003.3 |
AM |
Exception
1 should read "an area of refuge serving a stairway" |
| E36 |
1007.6.2 |
Allows
a smoke partition instead of a smoke barrier at elevator
lobbies |
AS |
Seems
like appropriate change |
| E37 |
1007.6.2,
1007.6.5 |
Excludes
smoke barriers around ares of refuge for smoke protected
seating |
? |
|
| E38 |
1007.8.4 |
Requires
directions to be posted at exterior areas of refuge.
Also adds requirements in the IFC to include assisted
rescue in evac. And fire safety plans |
AM |
Appears
OK except requirements for posting may lead occupants to
re-enter the building in an emergency. |
| E39 |
1008.1.1,
1008.1.4, 1008.1.5, 1008.1.5.1, 1008.1.6, 1008.1.7, 1008.1.8,
1003.5 |
Appears
to reconstitute language only |
? |
Necessary? |
| E40 |
1008.1.1.1 |
Adds
exception for door closers and door stops
as projections into clear width |
AS |
Appropriate
change |
| E41 |
1008.1.2 |
Allows
manual sliding doors for areas with occupant loads of 10 or
less |
AS |
Was
part of BOCA code |
| E42 |
1008.1.2 |
When
a pair of doors swing in opposite directions, the panel on the
right must swing in the direction of egress |
AS |
Appears
appropriate |
| E43 |
1008.1.2,
1008.1.3, 1008.1.3.1 |
Adds
subsection numbers to current text and makes minor
clarifications |
AS |
Seems
appropriate Will
require re-numbering of subsequent sections since 1008.1.3
currently exists. |
| E44 |
1008.1.3.1 |
Adds
language to revolving doors stating that they may not be used
as part of an accessible route |
D |
Not
necessary |
| E45 |
1008.1.3.4,
1008.1.8 |
Deletes
1008.1.3.4 "Access controlled egress doors" and adds
simplified language to 1008.1.8 for electrically locked egress
doors |
AS |
Simplified
language appears appropriate |
| E46 |
1008.1.3.5 |
New
section includes same language as second part of E45 put
leaves 1008.1.3.4 |
D |
In
favor of E45 |
| E47 |
1008.1.8.3 |
Adds
a number 5 to doors permitted to be locked from the egress
side, where fire doors lock after minimum temperature is
reached disabling the unlatching mechanism |
D |
Not
sure where this type of mechanism is used
or why we would consider allowing it in an egress door. |
| E48 |
1008.1.8.3 |
Allows
doors to be locked for some I2 uses where clinical needs
require security provisions for their safety provided staff
can readily open the doors |
D |
Language
leaves too much to interpretation.
Delayed egress locks are still an option. |
| E49 |
1008.1.8.6 |
For
delayed egress locks adds text after "capable of being
unlocked from a fire command center" if present or signal
by emergency personnel from a location inside the main
entrance" |
D |
Contrary
to the statement by proponent, this will increase costs, this
will require remote unlatching of delayed egress locks.
Current text only requires remote unlatching when a
fire command center is present (high -rise) |
| E50 |
1008.1.8.6 |
Delayed
egress locks - delete in item 4 "not more than 15
lbs" add "15 lbs or greater" |
D |
Proponent
has interpreted the text incorrectly |
| E51 |
1008.1.8.6.1 |
New
section allowing delayed egress locks as provided in
1008.1.8.6 to be locked in certain I2 uses without delayed
release if a keypad is provided |
D |
Too
much reliance on staff to open all egress doors in an
emergency. |
| E52 |
1008.1.8.7 |
New
section similar to1008.1.3.4 for all doors (not just main
entrance doors) |
AS |
Appears
to require the hardware to operate in the direction egress
when hardware is operated |
| E53 |
1008.1.8.7 |
Adds
"when discharging to the exterior" to exception1 to
clarify when stair doors may be locked from the non-egress
side |
AS |
OK |
| E54 |
1008.1.9 |
Adds
that assembly areas with occupant loads >= 50 regardless of
occupancy classification will have panic hardware |
AS |
Proponent
makes a good argument |
| E55 |
1009.1,
1009.3 |
Adds
a scoping section for stairs |
D |
Text
may be interpreted that provisions do not apply to non-egress
stairs |
| E56 |
1009.1,1010.5.3,
1012.7 |
Changes
minimum stair width to 35" measured between handrails |
D |
Not
convinced this change is necessary |
| E57 |
1009.3,
1009.3.1 |
Reconfigure
tread and riser exception for R3 and R2 dwelling units to
include accessibility requirements |
AS |
Seems
appropriate |
| E58 |
1009.3,
1009.3.3 |
Primary
change rearranges nosing requirements |
AS |
OK
change |
| E59 |
1009.3,
1009.4, 1009.4.1, 1009.4.2 |
Creates
the term "walk line" to stair requirements |
D |
Not
convinced this series of changes and new terminology is
necessary |
| E60 |
1009.3.2.1 |
Adds
a requirement for visual contrast on all stair treads |
D |
Certainly
will be undesirable in dwelling units |
| E61 |
1009.9.3 |
Adds
exception 3 allowing openings in solid risers to not be more
than 1.5 " |
D |
Contradiction
of terms "openings" in "solid"
risers |
| E62 |
1009.3.3 |
Exempts
solid risers for spiral and alternating tread stairs |
AM |
OK
for alternating tread stairs because of their limited
application. Contrary to proponent's statement, spiral stairs
are used quite often in residential occupancies |
| E63 |
1009.3.3 |
Permits
open risers in F, H and S occupancies except areas accessible
to the public |
AS |
Good
change |
| E64 |
1009.4 |
When
stair landings include wheelchair spaces they shall not
encroach on required width |
As |
Seems
to be an appropriate change |