Proposed Code Change Number
|
Recommended
Action
|
Comments
|
Impact
|
|
M67-06/07
|
AS
|
Correct standard and verbiage
|
Correction
|
|
M68-06/07
|
AS
|
More correctly reflects actual conditions
|
We get reports rather than witnessing a test
|
|
M69-06/07
|
AS
|
This will allow for a more practical cleanout
opening seal and cover.
|
None
|
|
M70-06/07
|
AS
|
This seems like a more logical format and is
user friendly and easy to understand. Should be approved with M71 as
recommended below
|
Code easier to use
|
|
M71-06/07
|
AM
|
I would recommend picking up the language in
M71 and adding it as #3 to M70 exceptions.
|
Puts back the listed and labeled duct
|
|
M72-06/07
|
D
|
We have always had space around this duct for
inspection purposes
|
Negative impact. Takes away some of our
inspection ability.
|
|
M73-06/07
|
D
|
This section is speaking to things contained in
the enclosure. The added verbiage is not.
|
Not necessary.
|
|
M74-06/07
|
D
|
In favor of M 70
|
|
|
M75-06/07
|
AS
|
This addition should pose no problems.
|
Allows for terminations to be closer
horizontally to buildings and property lines.
|
|
M76-06/07
|
D
|
I feel this is adequately covered in chapter 4.
This will add too many different requirements
|
Nothing gained. No special hazard.
|
|
M77-06/07
|
AS
|
This allows for the installation of appliances
as they are listed and manufactured.
|
Will eliminate appeals in this area.
|
|
M78-06/07
|
AS
|
I think this is aimed at stores like Sub-Way
that bake bead in their location w/o hoods
|
Clarifies intent.
|
|
M79-06/07
|
AS
|
If this is a problem, we should approve this
proposal. Literal enforcement would cause this to be an issue.
|
In most cases no impact.
|
|
M80-06/07
|
AS
|
Assuming the standard is approved.
|
Definitive reference.
|
|
M81-06/07
|
AS
|
No harm done here. May be better language.
|
Wordsmith
|
|
M82-06/07
|
D
|
Has merit, however, should be energy code
requirement and wording not good “vise-versa”
|
If needed, should be in the Energy Code.
|
|
M83-06/07
|
D
|
This requirement is not a part of the UL710
listing and labeling. It provided the installer and the inspector
with the air flow requirements so the hood will function properly.
|
OK as is we need this information
|
|
M84-06/07
|
D
|
If the air is clean to acceptable levels, we
should permit it to be re-circulated. The balance is unnecessary
work smithing.
|
This would take away design flexibility and in
some cases cause unnecessary usage of energy.
|
|
M85-06/07
|
AS
|
The introduction of this standard would be
appropriate if the standard holds up.
|
New standard in Code.
|
|
M86-06/07
|
AS
|
Allowing combustible dust to be collected
allows for an unnecessary explosion hazard and at a minimum should
have minimum design standards if permitted.
|
Presently this exception is not and should not
be in
Ohio
|
|
M87-06/07
|
D
|
Unnecessary change
|
None
|
|
M88-06/07
|
AS
|
Good Change to clarify intent.
|
Eliminates conflicts
|
|
M89-06/07
|
AS
|
Possibly clarifies code language
|
None
|
|
M90-06/07
|
D
|
Presently is and should remain in the building
code.
|
Potential conflicts between IBC &IMC
|
|
M91-06/07
|
AS
|
Fills void in IMC about # of fasteners required
and has more practical application language
|
IMC and IRC will be consistent
|
|
M92-06/07
|
?
|
Gives minimum requirement, but I’m not sure
this is necessary
|
AS or D either one works
|
|
M93-06/07
|
AS
|
Brings in appropriate standards and eliminates
unnecessary language
|
None
|
|
M94-06/07
|
AS
|
Introduces appropriate standards
|
None
|
|
M95-06/07
|
AS
|
Installation instructions already apply, but
someone needs this additional guidance
|
None
|
|
M96-06/07
|
D
|
Not practical or enforceable
|
Trying to inspect for something we can’t
control
|
|
M97-06/07
|
AS
|
Clarifies requirement
|
None
|
|
M98-06/07
|
AS
|
If standard holds up
|
Fills void in code
|
|
M99-06/07
|
D
|
This requirement is already addressed in
Chapter 4 (403.3.4) If standard is desired, it would more
appropriate to put it in Chapter 4
|
|
|
M100-06/07
|
AS
|
Recognizes, introduces another product into the
code.
|
End results with this product will be the same.
|
|
M101-06/07
|
?
|
Haven’t experienced any problems with the
present language.
|
Introduces new standards.
|
|
M102-06/07
|
?
|
I have no experience with Radon
|
|
|
M103-06/07
|
AM
|
Leave two openings as an option
|
Alternative method.
|
|
M104-06/07
|
D
|
In favor of 103
|
|
|
M105-06/07
|
AM
|
Leave two opening requirements
|
See AM on 104
|
|
M106-06/07
|
D
|
In favor of 103 & 105
|
|
|
M107-06/07
|
AM
|
Leave two opening option and add single opening
option
|
Companion Change
|
|
M108-06/07
|
D
|
We’ve seen this several times before.
|
Why have the IMC?
|
|
M109-06/07
|
D
|
We need the manufacturer’s installation
instructions required. Fireblocking is already addressed in the
building code.
|
|
|
M110-06/07
|
D
|
I think this is already addressed the way it
is.
|
Ain’t broke
|
|
M111-06/07
|
D
|
This is addressed in the manufacturer’s
installation instructions.
|
|
|
M112-06/07
|
D
|
Draft system may be necessary for the appliance
to function properly. The
installation and inspection should be governed by this code.
|
|
|
M113-06/07
|
AS
|
Introduces appropriate standard If the standard
holds up.
|
Appropriate reference
|
|
M114-06/07
|
AS
|
Introduces appropriate standard If the standard
holds up.
|
Appropriate reference
|
|
M115-06/07
|
AS
|
Adds two appropriate standards and references
one existing standard. The standards have to be reviewed.
|
Appropriate references
|
|
M116-06/07
|
D
|
This would eliminate the requirement for low
water cutoff if radiation is above the boiler. Leaks could result in
boiler damage and a potential safety hazard.
|
This would result in a minimal cost savings to
the contractor.
|
|
M117-06/07
|
D
|
Same reason as in 116. We are dealing with a
code requirement here and not a standard requirement. I see no
reason to eliminate safety provisions of the code simply because a
standard does not specifically call for them.
|
This would result in a minimal cost savings to
the contractor
|
|
M118-06/07
|
?
|
I am not familiar with these refrigerants.
Listen to testimony.
|
|
|
M119-06/07
|
D
|
Most of the standards sighted are relevant to
appliances. We already allow these appliances. I am not familiar
with a couple of the listings. This proposal seems very much like a
product endorsement.
|
|
|
M120-06/07
|
D
|
Designers will use this standard, but not
always. The proposal still allows for other means. I feel the code
language is ok the way it is.
|
This change would have no effect on the code.
|
|
M121-06/07
|
AS
|
Depends on the standard review…
|
|
|
M122-06/07
|
AS
|
Already used in the real world
|
|
|
M123-06/07
|
AS
|
Companion to 121. If 121 passes we need 123
|
|
|
M124-06/07
|
D
|
If this is to be allowed, we need the standard
to which they are manufactured. This would be a great opportunity
for knock-off fittings sold directly to consumers.
|
|
|
M125-06/07
|
AS
|
Companion to 122. If 122 passes we need 125
|
|
|
M126-06/07
|
?
|
Listen to testimony
|
|
|
M127-06/07
|
D
|
In favor of 129
|
|
|
M128-06/07
|
AS
|
Good addition to the code.
|
Addresses potential problem with every system.
|
|
M129-06/07
|
AS
|
Give exception for a practice that already
exists.
|
|
|
M130-06/07
|
D
|
This is a performance code. I think this
concept is good, but too prescriptive.
|
|
|
M131-06/07
|
AS
|
Depends on standard review
|
|
|
M132-06/07
|
?
|
Will depend on standards review………
|
|